E-Stop circuit - a bit confused....


 

Hi guys,

I am working on version 4.0 of my CNC controller board. One of the
things I wanted to clean up was the E-Stop circuit for this.

This is how I would like it to work...

E-Stop is pressed...

Power to Motors is cut-off
Power to Spindle motor is cut-off
A logic level signal goes to all motor control chips

As I am mixing high and low voltages here, I know there are special
precautions I must take so as to not let the genie out of the bottle.

This is what I think I should have to make it all work...

The E-Stop actuator will have to contactors in it, 1 for logic and
the other for the power circuits.

1) Logic E-Stop contactor. When depressed, it takes that signal to
ground. Each of the inputs on the AVRs are pulled high with 10ks.

2) Power E-Stop contactor. Using a normally closed contactor, this
is to ground. When the butten is depressed, it is open. This
ground signal will go to the coil side of a relay(s) that switch the
power circuits on/off.

This should give me double protection (logic is off & power is off)
and it should keep the logic level voltages sepperate from the power
voltages etc.

I am sure I have something wrong as I usually do, but that's why I'm
asking :-)

Chris


 

--- In Electronics_101@..., "lcdpublishing"
<lcdpublishing@...> wrote:

Hi guys,

I am working on version 4.0 of my CNC controller board. One of the
things I wanted to clean up was the E-Stop circuit for this.

This is how I would like it to work...

E-Stop is pressed...

Power to Motors is cut-off
Power to Spindle motor is cut-off
A logic level signal goes to all motor control chips

As I am mixing high and low voltages here, I know there are special
precautions I must take so as to not let the genie out of the bottle.

This is what I think I should have to make it all work...

The E-Stop actuator will have to contactors in it, 1 for logic and
the other for the power circuits.

1) Logic E-Stop contactor. When depressed, it takes that signal to
ground. Each of the inputs on the AVRs are pulled high with 10ks.

2) Power E-Stop contactor. Using a normally closed contactor, this
is to ground. When the butten is depressed, it is open. This
ground signal will go to the coil side of a relay(s) that switch the
power circuits on/off.

This should give me double protection (logic is off & power is off)
and it should keep the logic level voltages sepperate from the power
voltages etc.

I am sure I have something wrong as I usually do, but that's why I'm
asking :-)

Chris
There are standards. The normal Start-Stop circuit begins with a
normally closed Stop switch from one power rail to the junction of a
normally open Start switch and one side of the holding contacts. The
other side of the holding contacts connects to the other side of the
Start switch (they are in parallel, the holding contacts hold the
Start state) and this junction connects to one side of the coil. The
other side of the coil goes to common or ground. You really don't
want to switch an emergency circuit with a ground connection. Any
short circuit can simulate a ground connection.

The point is, it takes a specific action (pressing the Start button)
to get power but even the loss of power will cause the Stop function
to work. And the system won't restart.

A not particularly useful schematic is in Figure 7-16 here


Richard


Stefan Trethan
 

I like those circuits.

Installed a large contactor that way on my bench to switch everything on or off. When i get fed up with something i can punch the off button and it shuts down with a satisfying thump ;-)

ST

On Thu, 27 Apr 2006 01:14:05 +0200, rtstofer <rstofer@...> wrote:

There are standards. The normal Start-Stop circuit begins with a

normally closed Stop switch from one power rail to the junction of a

normally open Start switch and one side of the holding contacts. The

other side of the holding contacts connects to the other side of the

Start switch (they are in parallel, the holding contacts hold the

Start state) and this junction connects to one side of the coil. The

other side of the coil goes to common or ground. You really don't

want to switch an emergency circuit with a ground connection. Any

short circuit can simulate a ground connection.


The point is, it takes a specific action (pressing the Start button)

to get power but even the loss of power will cause the Stop function

to work. And the system won't restart.


A not particularly useful schematic is in Figure 7-16 here




Richard


 

Okay, will re-think my power-side E-Stop section. I believe I
understand what you are saying and it seems to coincide with what
actions I have used to power up big machines. Too bad I wasn't into
electronics when I worked for the machine builders, I could have
learned SO MUCH at that time :-(

Thanks Richard

Chris



There are standards. The normal Start-Stop circuit begins with a
normally closed Stop switch from one power rail to the junction of
a
normally open Start switch and one side of the holding contacts.
The
other side of the holding contacts connects to the other side of
the
Start switch (they are in parallel, the holding contacts hold the
Start state) and this junction connects to one side of the coil.
The
other side of the coil goes to common or ground. You really don't
want to switch an emergency circuit with a ground connection. Any
short circuit can simulate a ground connection.

The point is, it takes a specific action (pressing the Start
button)
to get power but even the loss of power will cause the Stop
function
to work. And the system won't restart.

A not particularly useful schematic is in Figure 7-16 here


Richard


 

Yes, that "Thump" is very satisfying when everything is going "wrong"!




--- In Electronics_101@..., "Stefan Trethan"
<stefan_trethan@...> wrote:

I like those circuits.

Installed a large contactor that way on my bench to switch
everything on
or off. When i get fed up with something i can punch the off button
and it
shuts down with a satisfying thump ;-)

ST