I almost didn't come home today - SAFETY!


 

开云体育

In a message dated 4/17/2004 9:43:34 PM Central Standard Time, ghidera2000@... writes:
Moral of the story - NEVER "make do" with wiring. If you're going to
use dangerous voltages in your projects, DO IT RIGHT or scrap the
project. The person you kill may not be yourself.
?
Did I hear "Wired in accordance with EEOC rules!" ? ? ?


 

This may be semi OT as it is electrical, not electronic.

I work as a stationary engineer for a municiple government. Part of
our duties is minor electrical work - things like changing lamp
ballasts, fixing broken outlets, changing electric motors etc.

Anyway, I got a work order this morning saying that one corner of a
florescent fixture was pulling away from the ceiling in a preschool
room.I looked and one corner was sagging down about 1/4". I grabbed
a ladder and went up to see what was happening. I touched the
fixture and *ZAP*. Not a big jolt, but my fingers were a bit numb
for 15 minutes or so.

Needless to say, the power went off REAL fast after that. I took the
lens off, the tubes out, and removed the ballast cover. First thing
I noticed was the lack of a ground wire... Not a loose ground - it
was completely missing!

Next thing I noticed was that the knockout was bare. No bushing was
installed at all! I grabbed the hot and sure enough, the sheet metal
had cut through the insulation and charged the entire fixture to 120
volts - WITH NO GROUND. Thankfully, I was using a wooden ladder and
had touched a painted portion of the light.

It doesn't end there either. I took the fixture completely off the
ceiling and in the process discovered that the installer had simply
used metal screws directly into acoustic ceiling tiles! No joists
above, no toggle bolts, not even stupid drywall plugs. What boggled
my mind was that this fixture had been there for at least 12 years
(as long as I've worked there). And the room above this is a
gymnasium. When people run around, the ceiling shakes so much that
aluminium angle was screwed onto the fixtures to keep the lenses
from falling out.

Still not finished! The junction box was 6" to the side of the
knockout they used so the wires were sandwiched between the ceiling
and the fixture then had to do a 90 through the (unbushed) knockout.
The junction box itself was not attached to anything. It just had a
piece of wood screwed to it so it wouldn't fall through the hole in
the ceiling tile.

As you probably guessed, yes, most of the wires are NOT in conduit,
they were just run along joists with staples. There was one wire in
conduit, which simply ended and the wire then did a 100 degree turn
and got fed into the junction box.

There were three sets of wires led into the box - each with a
ground. All of them were neatly wire nutted together... NOT attached
to the junction box OR the fixture.

I looked around the room, there are 12 other fixtures... Needless to
say, the big boss, the medium boss, the little boss, and everyone in
between has heard about it. That room is a death waiting to happen.

Moral of the story - NEVER "make do" with wiring. If you're going to
use dangerous voltages in your projects, DO IT RIGHT or scrap the
project. The person you kill may not be yourself.


 

开云体育

This is one of those scary stories that convinces governments to make sure that only licensed electricians should do electrical work. Even scarier is the possibility that the person who did the install probably WAS licensed.
?
??? ??? The Sinister Dragon
?

Sent: Sunday, April 18, 2004 12:41 PM
Subject: [Electronics_101] I almost didn't come home today - SAFETY!

This may be semi OT as it is electrical, not electronic.

I work as a stationary engineer for a municiple government. Part of
our duties is minor electrical work - things like changing lamp
ballasts, fixing broken outlets, changing electric motors etc.

Anyway, I got a work order this morning saying that one corner of a
florescent fixture was pulling away from the ceiling in a preschool
room.I looked and one corner was sagging down about 1/4". I grabbed
a ladder and went up to see what was happening. I touched the
fixture and *ZAP*. Not a big jolt, but my fingers were a bit numb
for 15 minutes or so.

Needless to say, the power went off REAL fast after that. I took the
lens off, the tubes out, and removed the ballast cover. First thing
I noticed was the lack of a ground wire... Not a loose ground - it
was completely missing!


Logic Research Electronics
 

开云体育

Hi,
?
I am registered as an electrician (for almost 20 years) and although there are some cowboys out there, such bad workmanship is not tolerated.
Not earthing any fitting is beyond a joke and can result in loss of practicing license and a huge fine which would pretty much ruin a person.
?
Get yourself checked out by a doctor as the effects of a shock (on your heart) can?appear several days after the shock.

----- Original Message -----
Sent: Sunday, April 18, 2004 6:44 PM
Subject: Re: [Electronics_101] I almost didn't come home today - SAFETY!

This is one of those scary stories that convinces governments to make sure that only licensed electricians should do electrical work. Even scarier is the possibility that the person who did the install probably WAS licensed.
?
??? ??? The Sinister Dragon
?
Sent: Sunday, April 18, 2004 12:41 PM
Subject: [Electronics_101] I almost didn't come home today - SAFETY!

This may be semi OT as it is electrical, not electronic.

I work as a stationary engineer for a municiple government. Part of
our duties is minor electrical work - things like changing lamp
ballasts, fixing broken outlets, changing electric motors etc.

Anyway, I got a work order this morning saying that one corner of a
florescent fixture was pulling away from the ceiling in a preschool
room.I looked and one corner was sagging down about 1/4". I grabbed
a ladder and went up to see what was happening. I touched the
fixture and *ZAP*. Not a big jolt, but my fingers were a bit numb
for 15 minutes or so.

Needless to say, the power went off REAL fast after that. I took the
lens off, the tubes out, and removed the ballast cover. First thing
I noticed was the lack of a ground wire... Not a loose ground - it
was completely missing!


Rod Baxter
 

开云体育

Unfortunately even experienced electricians can get caught. About 15 years ago I was installing a mainframe computer which had a large Frequency converter to run it, about 50 KVA. ?The inspector who came to check on the electricians work checked the output of the converter and said it wasn’t working. I grabbed his hand as he went to touch it and stopped him electrocuting himself. What he had done was use his phase rotation meter to check the output and it did not work at 400Hz which was the output of the converter. I used my meter and showed him it was working, he went a bit pale and left! I am not a licensed electrician but I suspect I know more about electricity (and the regulations) than some electricians unfortunately.

?

Anyone can make a mistake I guess, the trick is to make sure they are not fatal..

?

Sorry to be OT here, but I get upset at some of the stupid licensing regulations we have in this country.

?

Rod

?

-----Original Message-----
From: peter tremewen [mailto:Ptremewe@...]
Sent: Sunday, 18 April 2004 4:45 PM
To: Electronics_101@...
Subject: Re: [Electronics_101] I almost didn't come home today - SAFETY!

?

This is one of those scary stories that convinces governments to make sure that only licensed electricians should do electrical work. Even scarier is the possibility that the person who did the install probably WAS licensed.

?

??? ??? The Sinister Dragon

?

From: ghidera2000

Sent: Sunday, April 18, 2004 12:41 PM

Subject: [Electronics_101] I almost didn't come home today - SAFETY!

?

This may be semi OT as it is electrical, not electronic.

I work as a stationary engineer for a municiple government. Part of
our duties is minor electrical work - things like changing lamp
ballasts, fixing broken outlets, changing electric motors etc.

Anyway, I got a work order this morning saying that one corner of a
florescent fixture was pulling away from the ceiling in a preschool
room.I looked and one corner was sagging down about 1/4". I grabbed
a ladder and went up to see what was happening. I touched the
fixture and *ZAP*. Not a big jolt, but my fingers were a bit numb
for 15 minutes or so.

Needless to say, the power went off REAL fast after that. I took the
lens off, the tubes out, and removed the ballast cover. First thing
I noticed was the lack of a ground wire... Not a loose ground - it
was completely missing!

?


 

Sorry to be OT here, but I get upset at some of the stupid
licensing regulations we have in this country.
And how many more people would kill themselves or others if there
were no licensing or regulations?

An idea doesn't have to be perfect for it to still be a good idea.

Mike


--- In Electronics_101@..., "Rod Baxter"
<rod.baxter@b...> wrote:
Unfortunately even experienced electricians can get caught. About 15
years ago I was installing a mainframe computer which had a large
Frequency converter to run it, about 50 KVA. The inspector who
came to
check on the electricians work checked the output of the converter
and
said it wasn't working. I grabbed his hand as he went to touch it
and
stopped him electrocuting himself. What he had done was use his
phase
rotation meter to check the output and it did not work at 400Hz
which
was the output of the converter. I used my meter and showed him it
was
working, he went a bit pale and left! I am not a licensed
electrician
but I suspect I know more about electricity (and the regulations)
than
some electricians unfortunately.

Anyone can make a mistake I guess, the trick is to make sure they
are
not fatal..

Sorry to be OT here, but I get upset at some of the stupid licensing
regulations we have in this country.

Rod


 

开云体育

In a message dated 4/18/2004 3:00:47 AM Central Standard Time, logicresearch@... writes:
Not earthing any fitting is beyond a joke and can result in loss of practicing license and a huge fine which would pretty much ruin a person.
Yes, Logic.? But the Anglican Kingdom has retained common sense, while sadly, we Yanks have let a liberal mentality take that over, and, well, I dasn't go into that here, lest I be forced to try to explain a sociophenomenon I find too tedious to study sufficiently to argue.


John Johnson
 

Sorry this happened to you. I got stuck on 320v when I was a teenager,
fortunately my mother pulled me off of it. I was dying, and know it isn't any fun.

This is why everyone should use lock-out tag-out every time, without fail.
There should also be documented de-energizing procedures for every
device in the facility.

My company won't even buy the LOTO equipment for me.

Regards,
JJ

On Saturday, Apr 17, 2004, at 22:41 US/Eastern, ghidera2000 wrote:
Anyway, I got a work order this morning saying that one corner of a
florescent fixture was pulling away from the ceiling in a preschool
room.I looked and one corner was sagging down about 1/4". I grabbed
a ladder and went up to see what was happening. I touched the
fixture and *ZAP*. Not a big jolt, but my fingers were a bit numb
for 15 minutes or so.


Stefan Trethan
 

This is why everyone should use lock-out tag-out every time, without
fail.
Well, if you are only going to touch a thing like this lamp fixture which
should never ever be at dangerous potential it is hard to do that.

(e.g. where do you switch off before you touch the metal
fuse compartment for switching off the power.)

What i want to say is if one stupid guy is doing improper work you have most trouble
working after him.

One good idea would be to always use one of those screwdrivers with a indicator lamp.
it is by no means a 100% safety thing but it takes little enough time and work to touch
a chassis with it that you might actually use it.

Licensing is one possibility to keep certain standards,
but it is never perfect.

The dangerous thing is if people are forced to do things faster and cheaper
than they can be done properly.

ST


dangermouse
 

----- Original Message -----
From: "Stefan Trethan" <stefan_trethan@...>
To: <Electronics_101@...>
Sent: Sunday, April 18, 2004 2:29 PM
Subject: Re: [Electronics_101] I almost didn't come home today - SAFETY!



This is why everyone should use lock-out tag-out every time, without
fail.

What i want to say is if one stupid guy is doing improper work you have
most trouble
working after him.
True enough. My company had a simple, ironclad rule: no lockie, workie.
Period. Then one day I touch the negative side of a DC meter on a piece of
equipment that had been locked and tagged out. I got 120VAC to my
admittedly surprised finger, and one of those question-mark thingies
floating in the air above my head.

Some yahoo had figured the easiest way to interface a control unit across
the room was to run an independent 120VAC line to this control box, thereby
insuring that when we THOUGHT we were locked out, we weren't.

Oh--and he managed to reverse line and neutral while he was at it.

-DM


 

--- In Electronics_101@..., John Johnson <johnatl@m...>
wrote:
Sorry this happened to you. I got stuck on 320v when I was a
teenager,
fortunately my mother pulled me off of it. I was dying, and know
it
isn't any fun.

This is why everyone should use lock-out tag-out every time,
without
fail.
There should also be documented de-energizing procedures for every
device in the facility.

My company won't even buy the LOTO equipment for me.

Regards,
JJ
I had my lockout hanging on my belt actually. I never work on
electrical equipment without locking out and PROVING that the power
is off. In this case though, why would anyone lock out when you're
only looking at the fixture - without even taking the lens off?
Thats like saying you would need to lock out your table lamp at home
before you could touch it to turn it on or off.

This was installed prior to my employer hiring a full time
Electrician (same time I started). All work was done by electrical
contractors who are required to be licensed by law here. No ticky,
no worky! Being ticketed just means you know HOW to do things
correctly, not that you WILL do them that way.

Where I live, only a homeowner working on thier own home is allowed
to do electrical work without a license. Even then, they still have
to get permits and be inspected prior to energizing. The only reason
we're allowed to do the minor electrical work is that the employer
takes out an annual permit and we work under the direction of the
ticketed electrician. Any work we do is inspected by the electrician
and only the electrician is allowed to energize the circuit after
repairs/installation. He has to check out each person before they're
allowed to even pick a voltage tick, never mind actually touch a
power cord.


Rod Baxter
 

Mike, what I was saying (not very well) is that the English system is a
better way to go. It's not possible to stop people doing their own work,
no matter how much legislation or licensing is specified, so another way
needs to be found.
To me the obvious way is to let people do their own work, owner-builder
if you like, but insist they have it inspected cheaply before its
passed.

This will save lives, including those of future electricians who may
have to work on it later.

It wont make less work for any licensed electricians, as these
owner-builder types will do their own anyway, so lets encourage them to
get it inspected so no-one gets hurt.

Rod

-----Original Message-----
From: upand_at_them [mailto:upand_at_them@...]
Sent: Sunday, 18 April 2004 10:10 PM
To: Electronics_101@...
Subject: [Electronics_101] Re: I almost didn't come home today - SAFETY!

Sorry to be OT here, but I get upset at some of the stupid
licensing regulations we have in this country.
And how many more people would kill themselves or others if there
were no licensing or regulations?

An idea doesn't have to be perfect for it to still be a good idea.

Mike


--- In Electronics_101@..., "Rod Baxter"
<rod.baxter@b...> wrote:
Unfortunately even experienced electricians can get caught. About 15
years ago I was installing a mainframe computer which had a large
Frequency converter to run it, about 50 KVA. The inspector who
came to
check on the electricians work checked the output of the converter
and
said it wasn't working. I grabbed his hand as he went to touch it
and
stopped him electrocuting himself. What he had done was use his
phase
rotation meter to check the output and it did not work at 400Hz
which
was the output of the converter. I used my meter and showed him it
was
working, he went a bit pale and left! I am not a licensed
electrician
but I suspect I know more about electricity (and the regulations)
than
some electricians unfortunately.

Anyone can make a mistake I guess, the trick is to make sure they
are
not fatal..

Sorry to be OT here, but I get upset at some of the stupid licensing
regulations we have in this country.

Rod





Yahoo! Groups Links


Mike Rainone
 

开云体育

And what "sociophenomenon" would that be? Frankly, it is the conservatives that insist that what you do in the privacy of your own home is sacrosanct (of course, if you are gay that's something else entirely). Thus,?you should be able to wire or fry yourself?as you wish. Don't you find it interesting that those damn liberal states in the northeast have some of the most rigid "craft and licensing?laws" that are in fact?much like those in the "Anglican Kingdom" with all of their common sense??
?

----- Original Message -----
From: JanRwl@...
Sent: Sunday, April 18, 2004 3:03 PM
Subject: Re: [Electronics_101] I almost didn't come home today - SAFETY!

In a message dated 4/18/2004 3:00:47 AM Central Standard Time, logicresearch@... writes:
Not earthing any fitting is beyond a joke and can result in loss of practicing license and a huge fine which would pretty much ruin a person.
Yes, Logic.? But the Anglican Kingdom has retained common sense, while sadly, we Yanks have let a liberal mentality take that over, and, well, I dasn't go into that here, lest I be forced to try to explain a sociophenomenon I find too tedious to study sufficiently to argue.